Networking/Cable info request

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • McGuiver
    replied
    You could run fiber optic cable in the conduit with the AC power. It will not conduct power, and no cross talk. Use a media converter at each end if necessary...


    Sent from my iPhone using Tapatalk Pro

    Leave a comment:


  • Offspring
    replied
    Originally posted by FF90
    NO cat 5 / 6 should be a minimum of 3' from A/C wires, unless crossing at a 90 degree, Most Cat 5/6 is NOT shielded, and even with shielding a close parallel run is not recommended. Also NEC says do not mix high voltage and low voltage in same conduit
    This is correct by both practice and code.
    Even if you did you do it you then have the dance of not grounding the shield vs grounding one or both ends.

    Get a ubiquity wireless bridge.

    Leave a comment:


  • FF90
    replied
    NO cat 5 / 6 should be a minimum of 3' from A/C wires, unless crossing at a 90 degree, Most Cat 5/6 is NOT shielded, and even with shielding a close parallel run is not recommended. Also NEC says do not mix high voltage and low voltage in same conduit

    Leave a comment:


  • steve91104
    replied
    Not an electrician, but I believe having high and low voltage stuff in the same conduit can be a safety hazard.

    I don't think noise would be an issue though since the cable is shielded.

    Leave a comment:


  • hardlyworking
    replied
    I can terminate the ends of the cable, if there are particular cables you would recommend given the constraints, I'm all ears!

    Leave a comment:


  • hardlyworking
    started a topic Networking/Cable info request

    Networking/Cable info request

    Alrighty, its been a LONG time since physics, current through a wire causes a magnetic field, magnetic field creates a current in a wire etc...

    I have a workshop in the back of the property, with my reloading setup, wife's COVID office, tack-room for the horses etc.

    It has underground conduit from the main breaker box with a "fairly high" amperage circuit running 240V and 120V out to the workshop

    Can I fish some shielded CAT6 down that conduit and into the workshop from the main house?

    I mean, obviously I can, but will there be crazy cross-talk/packet loss/interference from the networking cable being inside and millimeters away from an active AC power lines in the conduit?

    The alternative is to just lay bare wire on the ground for 30 yards (or put it into some kind of above ground conduit) but that's going to drive the Mrs. crazy.

    Advice requested!
    Thanks guys!